Relay/Dimmer fuse protection...

Discussion in 'C-Bus Wired Hardware' started by skyline, Feb 21, 2006.

  1. skyline

    skyline

    Joined:
    Nov 23, 2005
    Messages:
    42
    Likes Received:
    0
    I know there are plenty of threads on this subject but there does not seem to be any I guess standards or commonly accepted methods. So I'll pose my scenario: Hardware is 3x L5512RVF's, 2x L5508D1A's and a L5504D2A. Space is not a major issue as I have 3 36-pole boards dedicated for this.


    Solution 1
    Install a seperate RCD/MCB for each unit, but have not been able to locate a 8a RCD/MCB for the dimmers. This setup gives maximum flexability.

    Solution 2
    Install one RCD/MCB and a seperate MCB for each unit. Again flexibility but if RCD trips, takes out all lighting.

    Solution 3
    Install an RCB/MCB for the relays and a seperate RCD/MCB with seperate MCB's for each unit. Probably a compromise of the above.

    Any feedback and product/capacity recomendations would be appreciated.

    Cheers
    Daniel
     
    skyline, Feb 21, 2006
    #1
  2. skyline

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    Solution 4
    Install a 10A RCD/MCB and not worry about the two amps

    Solution 5
    Install a 10A RCD/MCB and an 8A MCB for the dimmers. No discrimnation between the two though, not when they are that close together.

    Mick
     
    znelbok, Feb 23, 2006
    #2