relay failure

Discussion in 'C-Bus Wired Hardware' started by manni, Jul 17, 2007.

  1. manni

    manni

    Joined:
    Jul 15, 2007
    Messages:
    11
    Likes Received:
    0
    My electrical contractor and i installed the program database to the network last night and afterwards it looks like a relay failure. The buttons on the relay don't work anymore.
    The toolkit found all units on the network and it appeared to be talking properly.
    Would the programming (if set incorrectly) render the buttons on a relay inoperable or if this happens does it mean that the relay has failed?
    thanks again
     
    manni, Jul 17, 2007
    #1
  2. manni

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    It is possible to disable the buttons on the relay itself (these buttons are called "Local Toggle" keys) by unchecking the "Enable Local Toggle" checkbox on the "Global" tab.

    Does the relay respond to commands on the network?

    Nick
     
    NickD, Jul 17, 2007
    #2
  3. manni

    manni

    Joined:
    Jul 15, 2007
    Messages:
    11
    Likes Received:
    0
    relay

    it doesn't respond to program commands.
    and the enable local toggle is checked.
     
    manni, Jul 17, 2007
    #3
  4. manni

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    Are the "C-Bus" and "Unit" LEDs on the relay unit on?
     
    NickD, Jul 17, 2007
    #4
  5. manni

    manni

    Joined:
    Jul 15, 2007
    Messages:
    11
    Likes Received:
    0
    relay

    The upper LED stayed illuminated the bottom was off.
     
    manni, Jul 17, 2007
    #5
  6. manni

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    The bottom LED is the "C-Bus" LED.

    If this is off it means you will not have any comms to the unit on C-Bus.

    This could be for any of the following reasons :

    - your network is over or under burdened
    - you have no C-Bus clock enabled
    - the network voltage is low
    - the network is not connected at all

    I suggest you call tech support and they will walk you through getting it up and running again.

    Nick
     
    NickD, Jul 17, 2007
    #6
  7. manni

    manni

    Joined:
    Jul 15, 2007
    Messages:
    11
    Likes Received:
    0
    relay

    thanks Nick
    It was 2 in the morning, so we probably had something minor.
    The local keys were working fine before the upload of the program, then nothing.
     
    manni, Jul 17, 2007
    #7
  8. manni

    Darpa

    Joined:
    Apr 30, 2006
    Messages:
    426
    Likes Received:
    0
    Location:
    Australia
    Could you possibly have enabled or disabled a software burden in the changes you uploaded?
     
    Darpa, Jul 17, 2007
    #8
  9. manni

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    It could also be that no clocks were left enabled. If there's an output unit on the network then simply entering Learn Mode and exiting again will get you up and running if that's what happened.
     
    Newman, Jul 17, 2007