Discussion in 'C-Bus Toolkit and C-Gate Software' started by SparkyGreen, Aug 22, 2009.

  1. SparkyGreen

    SparkyGreen

    Joined:
    Aug 15, 2009
    Messages:
    1
    Likes Received:
    0
    Location:
    Hampshire England
    I am fairly new to C-Bus and would like some help -- Using a multisensor I am trying to bring on 3 groups of Outside Lights at approx 25% dusk till dawn then using individual PIRs for two groups I want to then bring that group up to 100% the multi sensor would ideally do the same to the third group -- when timed out I want the group that was activated by its PIR to return to the 25% level until dawn -- Help please:confused:
     
    SparkyGreen, Aug 22, 2009
    #1
  2. SparkyGreen

    joshl

    Joined:
    May 25, 2008
    Messages:
    68
    Likes Received:
    0
    correct me if im wrong but wouldnt you in toolkit in the pir settings on the blocks tab set the recall 1 level to 25% and the recall 2 level to 100% with a expiry of "ramp recall 1", and then in the functions tab make the MD shortpress a "recall 2" As for coming on for sunrise and sunset you could set the groups to come at a scheduled time of coming on at sunset and turning off at sunrise.
     
    joshl, Aug 23, 2009
    #2
  3. SparkyGreen

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Have a look at this post. It's not exactly the same application, but it might give you enough info to achieve what you want, or kick-start a few other ideas.
     
    Newman, Aug 24, 2009