Setting C-Bus Date and Time from C-Gate with a PAC Present

Discussion in 'C-Bus Toolkit and C-Gate Software' started by kiwi64ajs, Jan 12, 2014.

  1. kiwi64ajs

    kiwi64ajs

    Joined:
    Nov 15, 2008
    Messages:
    29
    Likes Received:
    0
    Hi Guys,

    I'm having a problem whereby the date and time on DLTs is being set from the PAC's clock which drifts slower over several weeks. In an attempt to correct this I have a PC running C-Gate full-time and have configured it to broadcast the time periodically as a time master by changing settings in the config file but the PAC doesn't seem to want to receive date and time updates and basically ignores the correct time from C-Gate on the PC.

    What do I need to do to configure the PAC and C-Gate so C-Gate is the time master and the PAC is not?

    Currently I connect to the PAC with PICED, and set the time manually to set the PAC and all the DLTs to the correct time.

    Regards

    Alex Shepherd
     
    kiwi64ajs, Jan 12, 2014
    #1
  2. kiwi64ajs

    kiwi64ajs

    Joined:
    Nov 15, 2008
    Messages:
    29
    Likes Received:
    0
    Can someone at Clipsal Support respond to this please? :)

    Perhaps my question should have been "How to make an always running C-Gate instance a Time Master?"
     
    Last edited by a moderator: Feb 2, 2014
    kiwi64ajs, Feb 2, 2014
    #2
  3. kiwi64ajs

    daniel C-Busser Moderator

    Joined:
    Jul 26, 2004
    Messages:
    770
    Likes Received:
    21
    Location:
    Adelaide
    Hi kiwi64ajs,

    As far as I know the PAC should accept the timekeeping messages.

    Can I ask what are the settings you have changed in C-GateConfig.txt?

    clock.master=no
    clock.mastermode=secondary
    clock.update-interval=30

    Are you able to confirm C-Gate is producing the timekeeping messages? Do you have a snippet from logs/event.txt?
     
    daniel, Feb 24, 2014
    #3
  4. kiwi64ajs

    kiwi64ajs

    Joined:
    Nov 15, 2008
    Messages:
    29
    Likes Received:
    0
    Code:
    Here are the settings from the C-GateConfig.txt file:
    
    #### clock.master:
    # Operate the clock application in master mode
    # Default Value: no
    # Scope:         network
    # Effective on:  closeopen
    ###
    clock.master=yes
    
    #### clock.mastermode:
    # Selects primary or secondard master mode
    # Default Value: secondary
    # Scope:         network
    # Effective on:  closeopen
    ###
    clock.mastermode=primary
    
    #### clock.update-interval:
    # Interval in minutes between clock and timekeeping messages
    # Default Value: 30
    # Scope:         network
    # Effective on:  closeopen
    ###
    clock.update-interval=30
    
    Yes Clock messages are being sent from the PC onto C-Bus and the above is what I have had configured for months - years even.

    In desperation I recently commented out the last line and restarted C-Gate and things have suddenly started working much better.
    Code:
    # clock.update-interval=30
    So either there is a problem with setting clock.update-interval or it causes some other bug to manifest or the default is NOT 30 and commenting it out actually changes the clock.update-interval value to another value that works with the PAC Clock primary/secondary logic.

    I get a daily indication of the difference between the clocks as my blinds open via the PAC Schedule at 7:00AM and my Alarm on my iPhone is set for 7:00 AM and they are now only a few seconds apart. Previously they could drift to be 5 or more minutes apart over the period of 1-2 months.

    So for now I think I'm running ok again but I think there is a bug or something deeper going on here than meets the eye.

    Regards

    Alex Shepherd
     
    kiwi64ajs, Feb 25, 2014
    #4
  5. kiwi64ajs

    Matty

    Joined:
    Oct 15, 2004
    Messages:
    131
    Likes Received:
    0
    Hi Alex,

    The PAC will accept time keeping messages and stop sending them.
    Here are the rules for which unit becomes the time master:

    In the past I have seen circumstances where clocks jump around, this was a symptom of network comms problems. One way to verify that all units are communicating happily is to use the 'reliability test' feature in the C-Bus Diagnostics Utility available from the cis downloads page. This utility will also show you which unit is broadcasting time messages and will indicate whether C-Gate is/isn't sending messages when its expected to.

    Regards,

    Matty
     
    Matty, Feb 25, 2014
    #5
  6. kiwi64ajs

    kiwi64ajs

    Joined:
    Nov 15, 2008
    Messages:
    29
    Likes Received:
    0
    Ok, yes that was what I was expecting
    Ah huh! I'll take a look at that and see if I can track down the issue.

    Alex
     
    kiwi64ajs, Feb 25, 2014
    #6
  7. kiwi64ajs

    daniel C-Busser Moderator

    Joined:
    Jul 26, 2004
    Messages:
    770
    Likes Received:
    21
    Location:
    Adelaide
    Out of interest what version of C-Gate are you using?

    Your config options look correct.

    I checked the C-Gate code and the built-in default is indeed 30 minutes. You can check this by deleting the entire config file, C-Gate will recreate it on startup with this value. Commenting out this line in the config file therefore should not have made any difference.

    One thing worth mentioning is that these are 'network' scope config options, which means C-Gate will copy them into your project tag file. So even if you are tinkering with the global config options there may be values inside your project file that are overriding them. You can open the .xml file in a text editor to check this.

    The C-Gate clock application code hasn't changed in many years, and goes something like this (where [30] is the value of clock.update-interval):

    If clock.master=yes, C-Gate will emit regular time updates.

    If mastermode=primary it will emit the first update [PCI address] seconds after startup, and then every [30] minutes after that. If it sees a time update from the network, it will reset its internal counter to wait another [30] minutes before it emits another update.

    If mastermode=secondary it will emit the first update about [2 * 30] minutes after startup, and then every [30] minutes after that. If it sees a time update from the network, it will reset its internal counter to wait another [2 * 30] minutes before it emits another update.

    In all this C-Gate does not actually change the PC time, it uses an offset to keep track of the network time wrt the PC time, and emits updates based on that offset. You can find out this value with the C-Gate command "get 254/223 Offset".

    NB: You can track all this in a level 9 log as C-Gate should emit a level 8 event message that begins with "[clock] date XXXXX" or "[clock] time XXXXX" whenever it receives a time update from the network, and a message beginning with "Setting date and time (master mode)" when it emits an update.

    To put all this together using the rules Matty describes, the physical units on the network and even the HG/S+ software should quickly begin to defer to a C-Gate configured as the primary time master as it is emitting updates more frequently than any of them.

    So as for why it suddenly started working after C-Gate was restarted, I have no answer to this. Which is why I posted the above in case it may help you work it out.
     
    Last edited by a moderator: Feb 27, 2014