Startup Issue

Discussion in 'C-Bus Wired Hardware' started by abg, Feb 7, 2010.

  1. abg

    abg

    Joined:
    Dec 25, 2007
    Messages:
    208
    Likes Received:
    2
    Location:
    Sydney
    I have two networks, with the second network having 30 shutter controllers all located together and their c-bus cables daisy-chained between each unit (so there is no' external' cabling in this network outside the box). There are three c-bus power supplies on the network, so power is not an issue. Clocks are enabled on the bridge and two shutter relays and the burden is enabled on the bridge.

    When this network is initially powered on more often than not, three or four of the relays will not come online ie: there is no c-bus or unit light. These can be units between other units, so the c-bus signal is passing through, to the next unit but the unit itself has no c-bus light on.

    In order to get all units with their c-bus and unit lights active and present on the network the power needs to be cycled three of four times. During each cycle different units go on and different units will stay off.

    On the other network, there are 9 relays, 15 dimmers, 34 key inputs etc etc (88 units in total). This network never appears to have a problem when first powered up.

    Is it something to do with the shutter controllers startup sequence? - too many of the same unit trying to do the same thing at the same time? Why would some units (and not always the same ones) not initialise whilst most others do and what does the power cycling do other than randomly allow them all to eventually come online?

    Thanks.

    P.S. Once all units are on the network is completely stable, so it is only the startup that is odd.
     
    abg, Feb 7, 2010
    #1
  2. abg

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Can you give a little more info about the install?
    - Firmware version of Shutter Relays
    - Firmware version of Bridge
    - Reported network voltages across the units
    - Version of Toolkit used to program them
     
    Newman, Feb 7, 2010
    #2
  3. abg

    abg

    Joined:
    Dec 25, 2007
    Messages:
    208
    Likes Received:
    2
    Location:
    Sydney
    Hi Newman,

    See below.


    Can you give a little more info about the install?
    - Firmware version of Shutter Relays
    28 are V2.0.00
    2 are V2.2.00

    - Firmware version of Bridge
    4.6.00

    - Reported network voltages across the units
    L5501RBC 2.0.00 Voltage=29.9V
    L5501RBC 2.0.00 Voltage=29.6V
    L5501RBC 2.0.00 Voltage=29.8V
    L5501RBC 2.0.00 Voltage=29.4V
    L5501RBC 2.0.00 Voltage=29.9V
    L5501RBC 2.2.00 Voltage=28.8V
    L5501RBC 2.0.00 Voltage=29.1V
    L5501RBC 2.0.00 Voltage=29.4V
    L5501RBC 2.0.00 Voltage=28.8V
    L5501RBC 2.0.00 Voltage=29.0V
    L5501RBC 2.0.00 Voltage=29.0V
    L5501RBC 2.0.00 Voltage=29.1V
    L5501RBC 2.0.00 Voltage=28.8V
    L5501RBC 2.0.00 Voltage=28.5V
    L5501RBC 2.0.00 Voltage=28.8V
    L5501RBC 2.0.00 Voltage=29.0V
    L5501RBC 2.2.00 Voltage=28.8V
    L5501RBC 2.0.00 Voltage=29.0V
    L5501RBC 2.0.00 Voltage=29.0V
    L5501RBC 2.0.00 Voltage=29.1V
    L5501RBC 2.0.00 Voltage=28.8V
    L5501RBC 2.0.00 Voltage=28.5V
    L5501RBC 2.0.00 Voltage=28.5V
    L5501RBC 2.0.00 Voltage=28.5V
    L5501RBC 2.0.00 Voltage=28.5V
    L5501RBC 2.0.00 Voltage=28.3V
    L5501RBC 2.0.00 Voltage=28.2V
    L5501RBC 2.0.00 Voltage=28.7V
    L5501RBC 2.0.00 Voltage=28.2V
    L5501RBC 2.0.00 Voltage=28.5V
    5500NB 4.6.00 Voltage=30.2V


    - Version of Toolkit used to program them
    1.10.9​
     
    Last edited by a moderator: Feb 8, 2010
    abg, Feb 8, 2010
    #3
  4. abg

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Suggest you give tech support a call. They have seen this before and have sorted it out in the past.
     
    Newman, Feb 8, 2010
    #4
  5. abg

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    abg let us know how you sorted it.
     
    Charlie Crackle, Feb 11, 2010
    #5
  6. abg

    abg

    Joined:
    Dec 25, 2007
    Messages:
    208
    Likes Received:
    2
    Location:
    Sydney
    Logged with CIS this afternoon. Will let you know how it goes.
     