I have been forced to use the 5104DTSI due to the demise of the C-Bus wall mounted temperature sensors. I am using two in conjunction with a Wiser. I have run into multiple levels of [B][U][I]?Oh crap?[/I][/U][/B]. I am controlling multi-zoned underfloor ?in slab? water heating. There is a header tank that sits at 40 degrees. When a zone requires heat, I turn on the appropriate pump and manifold to ensure the water is sent to the correct zone. The floors are laminated wood covering and the floor temperature must not reach or exceed 28 degrees or it will warp the laminated wooden floor. I have that basics working without issue. The problems arise when I start to consider the exceptions to the rules. 1/ What happens if one of the sensors fails or becomes disconnected. The DTSI appears to read ?0 degrees?. This in turn indicates to the Wiser that the room is freezing and will heat the floor up to 40 degrees and keep it there. (I have coded to disregard any 0-degree readings) There is error reporting available on the DTSI but I can find no references anywhere that tells me what the DTSI actually reports and under what conditions. [I][U]Can this be used to test if the sensor/s are present?[/U][/I] 2/ The next issue is what happens if I were to lose the DTSI from the network. If the heating is active when the unit is lost then I have a temperature runaway situation again. I will need to test if the DTSI is available for me to read to ensure the readings are valid. I have been unable to find any reference code that would enable me to perform this test. 3/ What happens should I lose the Wiser. This could occur if the circuit breaker trips the circuit that feeds the Wiser or the wiser becomes unplugged. If the heating is active then I am left in the situation once again. Does anyone have solutions to the above noting that the house is now complete and no further costs can be incurred. [B]Product suggestion for Clipsal:[/B] What would be nice would be to have a relay that has its own timer (Say 5 minutes in my case). The LOGIC would need to address the relay regularly to restart the timer to maintain the ON state. This way if the LOGIC disappears then the system would ?FAIL SAFE?. Yes this can be done in logic but any logic unit on the network is susceptible to the physical/ power loss scenario, so it needs to be part of the relay. [LIST] [*]This would address the issue if the relay unit itself becomes disconnected from the network. (Fails Safely) [*]If power to the relay is removed the relay again fails safely.[/LIST] At the end of the day ? Who is ultimately responsible for the floor replacement costs when this occurs?