Temporary Manual Operation

Discussion in 'C-Bus Wired Hardware' started by Leigh, Apr 17, 2007.

  1. Leigh

    Leigh

    Joined:
    Feb 2, 2005
    Messages:
    75
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Situation: New installation with all 240v wiring for lighting complete. C-Bus wiring installed but not terminated. Programming not commenced. Four output units (L5512RVF 12 channel relays & L5508D1A 8 channel dimmer).

    Question: To allow lights to be used during final stage of construction (painting etc) will it cause problems (now or later), if the painter is allowed to manually turns lights on and off using the local toggle indicators on the output units until C-Bus wiring and programming is complete?
     
    Leigh, Apr 17, 2007
    #1
  2. Leigh

    PSC

    Joined:
    Aug 3, 2004
    Messages:
    626
    Likes Received:
    0
    Location:
    Brisbane, Australia
    No problems with controlling C-Bus manually via the output unit local toggle buttons.
     
    PSC, Apr 17, 2007
    #2
  3. Leigh

    Darpa

    Joined:
    Apr 30, 2006
    Messages:
    426
    Likes Received:
    0
    Location:
    Australia
    I don't mean this in any condescending way, but thats pretty much one of the main reasons they are there :p
     
    Darpa, Apr 17, 2007
    #3