Terminating resistors needed on Cbus network?

Discussion in 'General Discussion' started by cbm_Craig, Jul 8, 2009.

  1. cbm_Craig

    cbm_Craig

    Joined:
    Jun 24, 2009
    Messages:
    14
    Likes Received:
    0
    Location:
    VIC
    Hi All,

    I've been forced (again) to ask a stupidly simple question by circumstances my installer (who obviously doesn't know what he is doing) has gotten us into and am prepared to take the flames as long as I can get an answer today.

    As per my last thread (cbus network wiring), the installer has now connected three legs of the cbus network in parallel with each other and connected to the cbus system. He is trying to scan the network and detect all the units but its not working unless he does a scan of each separate leg and even then hes not getting all the units. What he hasn't done is put a burden / terminating resistor (5500BUR) on the end of each leg, is it definitely necessary on the cbus network to terminate each branch of a network? I am thinking it is the problem but would like to hear other's opinions or 100% confirmation that it is the problem before taking a course of action as we have limited time to finish the installation (I am waiting on this network scan so that I can do the programming!).

    Cheers!

    Craig

    PS...sorry to those before in the other thread that were only trying to help me, I am doubly frustrated having to run around finding this basic fundamental sh$t out at the last moment when it should have been covered by the PM and electricians before the job even started!..I would greatly appreciate your help again ;)
     
    Last edited by a moderator: Jul 8, 2009
    cbm_Craig, Jul 8, 2009
    #1
  2. cbm_Craig

    ariddell

    Joined:
    Apr 20, 2009
    Messages:
    58
    Likes Received:
    0
    No, it doesn't need to be terminated at the end of each leg.

    The whole network should probably only have 1 "burden" going by the diagram you posted previously, this can be either a hardware one (5500BUR)or enabling the software seletable one on one of your modules. If you are using the physical one then check and make sure that the software burden is turned off on all modules through the c-bus toolkit. Personally i prefer not to use the physical one.

    Someone else will be able to tell you the exact way to identify number of burdens required for a network/best practise for how they should be configured wth hardware/software so i'm just going from my own experience on this one.

    Hope this helps.

    Cheers

    Al
     
    ariddell, Jul 8, 2009
    #2
  3. cbm_Craig

    cbm_Craig

    Joined:
    Jun 24, 2009
    Messages:
    14
    Likes Received:
    0
    Location:
    VIC
    Thanks Al,

    Just called him about it, turns out he had neither the hardware burden in or the software one enabled...got him to enable the software one in the PC interface module and see how that goes.

    He seems to be getting limited success doing one leg at a time but not all together (pre burden enabled), he has a theory (god help us, we really need someone that knows what they are doing at this point, not theories but its what we've got to work with :() that if he can't get it to work with all the legs in parallel then he will wire it so that the network loops back through the same cat5 cable using 2 unused wires within the cable...don't know if that makes sense or is possible but he's basically experimenting until he gets it all to work :S

    Cheers!

    Craig

    PS...so I think something like this...(network 1 and 2 are the legs, not separate cbus networks ;))

    [​IMG]
     
    Last edited by a moderator: Jul 8, 2009
    cbm_Craig, Jul 8, 2009
    #3
  4. cbm_Craig

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    God help you indeed. Please tell him NOT to do this... it should not be necessary and is likely to cause more than it solves (and the likelihood that it will actually solve anything is low). Tell him to stick with using the recommended cores (blue + orange for C-Bus positive and blue/white + orange/white for C-Bus negative).

    There should be at most ONE burden required. Depending on how many units you have attached, you may not need one at all. If he is splitting the networks and testing them individually then make use he has a burden active or attached to the network he is scanning.

    How many devices are on each of the networks?

    Nick
     
    NickD, Jul 8, 2009
    #4
  5. cbm_Craig

    daniel C-Busser Moderator

    Joined:
    Jul 26, 2004
    Messages:
    770
    Likes Received:
    21
    Location:
    Adelaide
    As far as c-bus is concerned all of that is one network. How many units in total across all the "legs"?

    The fact that you have not just simply wired Leg #2 into one of the units on Leg #1 suggests they may be quite far apart physically, is this the case? What is the total cable run?
     
    daniel, Jul 8, 2009
    #5
  6. cbm_Craig

    filpee

    Joined:
    May 31, 2006
    Messages:
    204
    Likes Received:
    0
    Location:
    Western Australia
    Sounds more like a power issue then a burden problem.

    Too much cable, or too many devices on each leg dragging the network down.

    Check your voltages.
     
    filpee, Jul 8, 2009
    #6
  7. cbm_Craig

    cbm_Craig

    Joined:
    Jun 24, 2009
    Messages:
    14
    Likes Received:
    0
    Location:
    VIC
    Yeah they are physically far apart, there are 32 devices all up...originally there were 6 and another 26 have been added, he is currently able now to successfully scan 27 of them but as soon as he adds the other "leg" on with the final 5 devices it crashes the network...so I'm assuming a bridge is required?

    I have gotten him to enable the software burden in the pc interface module through which he has been test scanning each leg, the hardware burden isn't being used.

    Cheers!

    Craig
     
    cbm_Craig, Jul 8, 2009
    #7
  8. cbm_Craig

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    How many relays/dimmers with power supplies are there?
    How many standalone power supplies?
    What are the other units that have been added?

    Can you get the installer to measure the bus voltage before and after he connects the final leg that causes it all to fall over?

    Nick
     
    NickD, Jul 8, 2009
    #8
  9. cbm_Craig

    cbm_Craig

    Joined:
    Jun 24, 2009
    Messages:
    14
    Likes Received:
    0
    Location:
    VIC
    There's a relay with its own power supply at the start of each leg, there are no standalone power supplies as such just one PC module, 2 input modules, 2 output modules and a HMI, the new 26 units are 25 x 4 pole change over relay units (5504RVFC) and 1 x 4 button plate switch (B5034NL). All 25 relay units are connected to 240v as such to provide power for the changeover and the first on each leg is supposedly one that provides a boost to the network. That's the way he explained it to me anyway.

    I am waiting for them to test the bus voltage which I thought would have been the first thing they would do when suspecting a bus voltage drop issue. :rolleyes:

    Cheers!

    Craig
     
    cbm_Craig, Jul 8, 2009
    #9
  10. cbm_Craig

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    Whoa! Can you confirm whether these are L5504RVFC or L5504RVFCP?

    If they are L5504RVF, then you have 25 x 200mA = 5A of power supplies on your network, which is a big no-no (the limit is 2A), and may well be causing your communications problems. I'm hoping that by "one that boosts the network" he means that only one of the units on each leg has a power supply.

    The other thing to check is that you only have 2 or 3 clock generators activated... if you have all 25+ output units enabled as clock generators it may be taking a long time for the clock arbitration to finish when the network is powered up or when the new legs are connected/disconnected.

    Nick
     
    Last edited by a moderator: Jul 8, 2009
    NickD, Jul 8, 2009
    #10
  11. cbm_Craig

    cbm_Craig

    Joined:
    Jun 24, 2009
    Messages:
    14
    Likes Received:
    0
    Location:
    VIC
    According to the PM, there are 22 x L5504RVFCP and 3 x L5504RVFC. (going on what he has said to me, I assume he believes the 3 RVFCs are the ones that boost the signal/power...to me going by the model numbers I think its the wrong way round if that's even what they are supposed to do? I am thinking a bridge (5500NB) is in order?)

    In regards to the cbus clock, currently only the pc module has it enabled...I just restored a backup of the project with 21 of the 25 relay modules scanned and all of them have the clock disabled.

    He's got some other ideas on how to get it to work tomorrow, if your able to give me a solution before he "tries" them that would be awesome ;) :rolleyes:

    Cheers!

    Craig
     
    Last edited by a moderator: Jul 8, 2009
    cbm_Craig, Jul 8, 2009
    #11
  12. cbm_Craig

    darrenblake

    Joined:
    Nov 1, 2004
    Messages:
    151
    Likes Received:
    0
    Location:
    Melbourne
    C-Bus installation

    CBM Craig,

    Do yourself a favour and contact one of the Appproved Installers or pointOne members straight away!!!!

    You can find them listed on the CIS website

    It appears you are here in Melbourne. There are a number of very professional, competent companies who can help.

    It is very obvious your sparky has no idea.

    This will undoubtedly lead to a poor installation, poor functionality, poor reliability, and ultimately a poor experience for you and your family.

    Unfortunately, many electricians who attend a three day training course profess to be EXPERTS. I have spent many years helping contractors out of the sh*t with C-Bus.
    Having said that, there are a number of very good sparkies who are very competent.

    You will have to live with the technology for many years, give yourself a chance to enjoy the experience.
     
    darrenblake, Jul 8, 2009
    #12
  13. cbm_Craig

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,397
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    Sounds to me like it might be a basic wiring issue.

    You should not need a bridge with that number of units. It sounds like you have less than 1 km of cable, so again you dont need a bridge for that.

    If you have it partly working, then add the next portion on and it stops, then check the portion that, when added, breaks it.

    Check for wiring, termination / joining of the cable where it goes in and out of switches, remove units a few at a time. Try and isolate where the problem is by adding and/or removing things.
     
    ashleigh, Jul 8, 2009
    #13
  14. cbm_Craig

    cbm_Craig

    Joined:
    Jun 24, 2009
    Messages:
    14
    Likes Received:
    0
    Location:
    VIC
    Thanks Darren and Ashleigh,

    Its not actually for my house or any house, and I can't divulge details on the actual project...plus I'm not in Melbourne, I am in Victoria but the project is in Melbourne :p

    There is a PM (project manager) running the whole show and doing a lot of the work himself along with the electricians...but he obviously doesn't really know what he's doing :mad: I've tried to hint at him to call Tech Support and then maybe they will say to get an approved installer out there but Im not in a position to outright tell him what to do ;) Because I had some experience working with the cbus system that runs the lighting in my office I was contacted by this PM from our other office to do the programming work and now for some reason he contacts me on every problem he comes across including the wiring which I have ZERO experience with but am slowly learning the fundamentals through this whole situation :rolleyes:

    Current status is he has now been able to detect the 4 button plate switch after doing something funky with the wiring (im pretty sure he hasn't tried to loop back through the same cable yet though) so all that remains are 4 of the 4 pole changeover relay modules to detect.

    Im kinda at my wits end with the whole thing, being the 3rd link in the problem solving chain when he should just bloody call tech support or get someone qualified out there.

    Cheers for everyone's help :cool: