    How would I normally go about setting a condition, based on the time of day, for PIR operated lights to have 2 different max levels.


    100% up till midnight and then 50% from 12am to 5am.

    What is the current method ? I was previously under the impression it was done with MINDER or CLOCK UNIT but there must be newer ways now.
     
    tobex, Oct 15, 2010
    #1
  2. tobex

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    787
    Likes Received:
    74
    Location:
    Adelaide, South Australia
    You can do this in a device that has logic. PAC, B&W MKII touchscreen, C-Touch Spectrum, Wiser or C-Touch Colour
     
    Conformist, Oct 16, 2010
    #2
  3. tobex

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    The easiest way is to use logic in the output unit. On the Logic tab use MIN logic to link the dimmer channel to a logic group. Then, using a device capable of Schedules, as Chris lists, set this logic group to 50% at midnight and to 100% at 5am.

    B&W Touchscreens are available with and without logic capability and, by using Schedules, you can do this with either type of unit.
     
    Last edited by a moderator: Oct 17, 2010
    Newman, Oct 16, 2010
    #3
  4. tobex

    tobex

    Joined:
    Nov 3, 2006
    Messages:
    728
    Likes Received:
    0
    Location:
    Sydney, Australia
    I am looking at how it can be retrofitted to a very early system and I like your idea very much. What about a timed dry contact (powered timer) and a C-Bus coupler ? This is a very crude analog design but I wonder if it may work. It has the potential to open c-bus to an outside input. All comments welcome.
     
    Last edited by a moderator: Oct 16, 2010
    tobex, Oct 16, 2010
    #4
  5. tobex

    2SC

    Joined:
    Oct 10, 2006
    Messages:
    345
    Likes Received:
    0
    Location:
    Athens, Greece

    Great news that C-Touch Spectrum is available in AUS.
    I checked in local sites and the price is the same as the B/W ones.
    Is there any leaflet available except the one included in PICED?
     
    2SC, Oct 16, 2010
    #5
  6. tobex

    tobex

    Joined:
    Nov 3, 2006
    Messages:
    728
    Likes Received:
    0
    Location:
    Sydney, Australia
    What does the average touch screen cost ?
     
    tobex, Oct 16, 2010
    #6
  7. tobex

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    It would be possible to configure a bus coupler so that when it detected a contact closure it set the level of a group to, say, 50% using a Recall, and also started a 5 hour timer. The timer expiry event could be configured to a second Recall of 100%.

    You would, of course, need a method of triggering the bus coupler input at midnight.
     
    Newman, Oct 16, 2010
    #7
  8. tobex

    tobex

    Joined:
    Nov 3, 2006
    Messages:
    728
    Likes Received:
    0
    Location:
    Sydney, Australia
    Yes that is what I wanted to hear. I think that any conventional timer, even ones where you are able to operate a small LCD, can operate a changeover relay. This includes alarm panels and many other timer operated devices.

    The analog aspect is nothing special. Can be one of many.

    I might need some guidance on the coding aspect. Whilst I am familiar with the terms being described I am not 100% familiar with the actual parameter configuration.

    I am using a number of PIR indoors. I always use them in the shower, bathroom and laundry because these are places where people are always moving around or carry something in their hands. I always put PIR lights in the garage too. I cant see anyone getting out of a car to switch off the lights after they leave.

    Just some thoughts !

    If you have time would you be able to make me a screen shot of a viable setup ?
     
    tobex, Oct 17, 2010
    #8
  9. tobex

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    No rocket science here, just programming up of standard units.

    Dimmer programmed to use the Minimum of 2 groups, the Toilet Light group and the Brightness Limit group.

    Bus Coupler programmed to set the level of the Brightness Limit group to 50% (Recall 1) when the button is first pressed and then start a 5 hour timer. When the timer expires, set the brightness to 100% (Recall 2).
     

    Attached Files:

    Newman, Oct 17, 2010
    #9
  10. tobex

    tobex

    Joined:
    Nov 3, 2006
    Messages:
    728
    Likes Received:
    0
    Location:
    Sydney, Australia
    That is truly awesome. Thank you. I can understand and follow this example clearly.

    I notice that there are a number of DIN mounted timers. What I do look forward to is making the C-bus interact with the Alarm system PIRs or Camera recording motion alarms to execute late night "sleep-walker" lighting. The kind of lighting you need when you are half awake in the middle of the night.

    I can also use a spare VFR and have a "night mode" for the house.

    Many ways to do it !

    I imagine that the timer function on the C-Bus PIR does not interfere with the timer function on the logic group. I see that the C-Bus PIR is only addressing the lighting channel and nothing else.

    So then if I am using a mechanical changover relay with an external timer (not in the network) I can have the C-Bus determine if the relay is closed and use the LONG PRESS function without a timer. As soon as the Long Press mode is released then the lights go back to full power (subject to PIR demand).
     
    Last edited by a moderator: Oct 17, 2010
    tobex, Oct 17, 2010