Toolkit 1.11.9 Issue with 2 Channel Relays

Discussion in 'C-Bus Toolkit and C-Gate Software' started by MHeaton, Oct 19, 2011.

  1. MHeaton

    MHeaton

    Joined:
    Apr 22, 2008
    Messages:
    106
    Likes Received:
    2
    Location:
    London
    Hi,
    With Toolkit 1.11.9 the 2 channel relay shows up as a Serial Number mismatch on the Network view (it doesn't have a serial number).

    Deleting the unit in the DB and reloading it from the network doesn't solve the problem.

    Thanks
    Mark
     
    MHeaton, Oct 19, 2011
    #1
  2. MHeaton

    george

    Joined:
    Jul 26, 2004
    Messages:
    158
    Likes Received:
    1
    Location:
    Adelaide
    Hi Mark,

    We know about this issue but it cannot be fixed reliably. In case with C-Bus mask 1 units like 2-channel relay, we can only assume that if unit type and address of the unit in the database are the same as on the network then we have a match. This assumption will be most likely correct if we have only one 2-channel relay, however if there are 2 or more 2-channel relay units on the network, matching them with the database records suddenly turns into a challenge, if you take into consideration unravel moving units without serials to random addresses.

    Perhaps we can change the text of the error message to something less confusing, but without S/N we can't claim a reliable match. So for now please ignore Toolkit reporting S/N mismatch for units that don't have them.

    Regards,
    George
     
    george, Oct 19, 2011
    #2