Toolkit not opening network with CNI2?

Discussion in 'C-Bus Toolkit and C-Gate Software' started by fleetz, Aug 24, 2017.

  1. fleetz

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,319
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    Best wishes.
     
    DarylMc, Aug 26, 2017
    #21
  2. fleetz

    jonnyp64

    Joined:
    Dec 18, 2016
    Messages:
    50
    Likes Received:
    2
    Location:
    Sydney
    I had an almost identical problem last year. Kept scratching my head also until i realised that the CNI only allows one connection at a time and we had a C4 controller on the project. Maybe you have something similar??
     
    jonnyp64, Aug 27, 2017
    #22
  3. fleetz

    fleetz

    Joined:
    Nov 21, 2005
    Messages:
    362
    Likes Received:
    9
    Hi Jonny,

    Thanks for the feedback. I was aware that only one connection is allowed at a time to a CNI. That said I wonder why the C-Bus Diagnostic Utility reports "Connection already in use" ?

    Doing this at bench at home, there is no other Clipsal device or other product for that matter that would look to control a C-Bus Ethernet network ( C4, Ness etc).

    I have ensured that the IP address assigned to the CNI is not in conflict with any other on the network. I have tried two other IP addresses which are no where near other used IP address on my network. Made sure I am using the correct gateway and subnet mask etc.

    Ensured TK is trusted by Windows Firewall....

    I can see the CNI on the network when I ping all on the network. I can remove the CNI and it disappears and nothing else is on that address. I can ping the CNI and I get a correct response. I can connect to the CNI via the C-Bus IP Utility which doesn't use C-Gate.

    I have done a complete install of 1.15.2 with the associated version of C-Gate.

    All I have on the bench is the CNI2 other that the 12vDC power supply nothing else is connected to the unit. No C-Bus devices just Ethernet via a switch. Could not be simpler.
     
    Last edited by a moderator: Aug 27, 2017
    fleetz, Aug 27, 2017
    #23
  4. fleetz

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    Maybe a dumb question, but have you tried power cycling the CNI?

    They have been known to hold onto the connection even if the client has dropped it.

    Nick
     
    NickD, Aug 28, 2017
    #24
  5. fleetz

    fleetz

    Joined:
    Nov 21, 2005
    Messages:
    362
    Likes Received:
    9
    No question is ever dumb Nick...I power cycled lots of times over the last day or so. Also reset the unit a number of times.

    Thanks for hopping in with your suggestion...
     
    fleetz, Aug 28, 2017
    #25
  6. fleetz

    fleetz

    Joined:
    Nov 21, 2005
    Messages:
    362
    Likes Received:
    9
    Problem now is sorted.

    I needed a powered C-Bus network on the CNI and it connected with no issue.

    I blew the dusted off a faulty relay unit that had a power supply that been in a lightening strike event located a shorted Zener protection diode, lifted that and the C-Bus port woke up again. Connected that to the CNI and viola it connects without any issue.

    Thanks to Mr Mark for pointing it out. Thanks also to all that helped out...special call out to DarylMc who went above and beyond to help...cheers DarylMc

    I should have remembered my C-Bus training and the requirement for clock and burden. Also I should have never assumed the Ethernet and C-Bus networks were agnostic to each other.

    Anyway feedback for anyone else who tries to the same as me.

    Cheers,

    Ian
     
    fleetz, Aug 28, 2017