Touch Screen & Solar DC charge voltage

Discussion in 'General Discussion' started by industeq, Jun 7, 2010.

  1. industeq

    industeq

    Joined:
    Feb 8, 2009
    Messages:
    95
    Likes Received:
    0
    Location:
    Stafford, TX (Houston) USA
    Newbie and just learning PICED.
    I was wanting to see if there was a simple way to show a voltage of my solar battery bank on the BW Mark II ?
    Instead of me going to the garage and checking the Solar controller I could just look at the C-Bus in the AC controlled living room.
     
    industeq, Jun 7, 2010
    #1
  2. industeq

    Aaron

    Joined:
    Jul 16, 2009
    Messages:
    99
    Likes Received:
    0
    Location:
    Wales, UK
    Aaron, Jun 7, 2010
    #2
  3. industeq

    industeq

    Joined:
    Feb 8, 2009
    Messages:
    95
    Likes Received:
    0
    Location:
    Stafford, TX (Houston) USA
    industeq, Jun 7, 2010
    #3
  4. industeq

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    If you use the general input unit to read the voltage, I would set it up to broadcast this on the C-Bus Measurement application.

    In your PICED project, you then add this measurement channel to you project in the Measurement manager, and then add a component to the screen (a bargraph, or text component). In the component properties, under the SystemIO tab, select Key Function "Status" and an Inbuilt System IO type of "Measurement App Real Value". Then choose the channel you assigned in the measurement manager.

    HTH,

    Nick
     
    NickD, Jun 8, 2010
    #4
  5. industeq

    industeq

    Joined:
    Feb 8, 2009
    Messages:
    95
    Likes Received:
    0
    Location:
    Stafford, TX (Houston) USA
    Thanks Guys

    Do I attach the 12V DC Battery wires direct to one of the inputs on the General Input Unit?

    This seems to simple......:)

    I need to get my hands on a General Input Unit then try.

    Regards
    Alan Dobbs
     
    industeq, Jun 10, 2010
    #5
  6. industeq

    Darpa

    Joined:
    Apr 30, 2006
    Messages:
    426
    Likes Received:
    0
    Location:
    Australia
    Pretty much, Yes.

    A few things to watch out for though:
    The max voltage you can feed into the GIU is 20v, so if your battery bank is 24v or 48v, then change my yes above to a NO. (Yes, I have noticed you said 12v DC above, but thought I should mention it anyway).
    If you can't place the GIU within close proximity to the battery bank, then make sure you size the cable appropriately to minimise voltage drop.
    Also, make sure you place the smallest rated fuse you can as close to the battery as possible, to protect against one of those unpredictable issues that may arrise in the future.
     
    Last edited by a moderator: Jun 10, 2010
    Darpa, Jun 10, 2010
    #6
  7. industeq

    industeq

    Joined:
    Feb 8, 2009
    Messages:
    95
    Likes Received:
    0
    Location:
    Stafford, TX (Houston) USA
    What are the options for if I have a 24 VDC or a 48VDC bank...In the future I will have a 24VDC aling with the present 12VDC.

    since the batterys are in series to achieve 24VDC can 2 inputs across each plus / minus be wired then some logic inside to add the sum value for the total value to be displayed.


    Regards
    Alan Dobbs
     
    industeq, Jun 22, 2010
    #7
  8. industeq

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    The General Input unit supports scaling of the voltage, so you would just use a few resistors to scale the voltage down to within the input range of the GIU, and then apply the appropriate scale factor to compensate for this.

    Nick
     
    NickD, Jun 23, 2010
    #8