Transformer Input Capacitance?

Discussion in 'C-Bus Wired Hardware' started by discjockeyr, Oct 17, 2008.

  1. discjockeyr

    discjockeyr

    Joined:
    Jan 9, 2007
    Messages:
    59
    Likes Received:
    0
    Hi there,

    I have purchase some transformers to use with the 2Amps leading edge dimmer L5504D2A. Unfortunately there is no information written on the transformer regarding Transformer Input Capacitance. The details that i have is as follows:
    EUROPOWER
    Dimmable
    MODEL:KT-60MS
    20-60W/VA
    Pri:220-240V-50-60Hz 0.25A
    Sec:11.4V~eff,5A
    Cos(phi)=0.98

    I supposed that by dimmable means that can be use with leading edge dimmers but how can i found about capacitance? i did not find any information on the internet regarding this brand/model. Anybody also knows if the capacitor is in parallel with the 240V? i have open one unit and i did not see any capacitos in parallel with 240V but only one that is between 240V and 12V.
    Waiting for the experts advice :)
     
    discjockeyr, Oct 17, 2008
    #1
  2. discjockeyr

    discjockeyr

    Joined:
    Jan 9, 2007
    Messages:
    59
    Likes Received:
    0
    Seems that nobody can advise me regarding this matter?
     
    discjockeyr, Oct 19, 2008
    #2
  3. discjockeyr

    Pink Panther

    Joined:
    Jul 1, 2007
    Messages:
    26
    Likes Received:
    0
    Location:
    Auckland, New Zealand
    Transformer Input Capacitance

    Went through similar angst. Not all transformer specs cover input capacitance. Have called manufacturers reps in the past and they're not even sure what input capacitance is. My advice; Don't go for the cheapest transformers ... you only get what you pay for. The Tridonic Atco Possum's are a good choice for C-Bus.

    CIS used to test transformers for compatibility with their dimmers, but believe this no longer happens because there are far too many trannies in the market.

    You'll need to push the manufacturer for details on this characteristic. It's not the responsibility of the dimmer manufacturer to test every transformer for suitability.
     
    Pink Panther, Oct 19, 2008
    #3
  4. discjockeyr

    discjockeyr

    Joined:
    Jan 9, 2007
    Messages:
    59
    Likes Received:
    0
    Hi Panther,

    Thanks for your reply. Do you know if the capacitor is in parallel with the 240V input? I am asking so if is like that then we can measure it with capacitometer, otherwise we have to get the informations from the manufacturers which seems to be difficult.

    Thanks
     
    discjockeyr, Oct 20, 2008
    #4
  5. discjockeyr

    Pink Panther

    Joined:
    Jul 1, 2007
    Messages:
    26
    Likes Received:
    0
    Location:
    Auckland, New Zealand
    Transformer Input Capacitance

    Again, that's a question you'd have to ask the transformer manufacturer. You'll save yourself a lot of time and effort by using the Tridonic ATCO Possum trannies. We settled on these as a standard pretty early on and they never gave us any problems. They may not be the cheapest on the market but they'll maintain the quality and value of a C-Bus installation. From memory, they had one of the lowest input capacitance ratings of all the trannies CIS tested. (And no, I don't work for Tridonic!)
     
    Pink Panther, Oct 20, 2008
    #5
  6. discjockeyr

    discjockeyr

    Joined:
    Jan 9, 2007
    Messages:
    59
    Likes Received:
    0
    Thanks again for your reply Panther.
    Unfortunately i found that the specific brand can be found only on Australia. what about europe, is there any online shop that i can purchase trannies which have low capacitance? Also with Tritonic i may still have a problem as i have 8 halogen so i need 8 which Tritonic are rated on 33nF and i can use only 6.
     
    discjockeyr, Oct 21, 2008
    #6
  7. discjockeyr

    Pink Panther

    Joined:
    Jul 1, 2007
    Messages:
    26
    Likes Received:
    0
    Location:
    Auckland, New Zealand
    Pink Panther, Oct 21, 2008
    #7
  8. discjockeyr

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    Alternatively you may be able to find a transformer which you can fit more than one lamp to (which probably increases your overall efficiency as well)... eg

    2 x 35W lamps on a 70VA transformer
    3 x 35W lamps on a 105VA transformer
    2 x 50W lamps on a 105VA transformer

    Nick
     
    NickD, Oct 22, 2008
    #8
  9. discjockeyr

    discjockeyr

    Joined:
    Jan 9, 2007
    Messages:
    59
    Likes Received:
    0
    Dear Panther i have seen those documents but are very old and since then there are a lot of other brands in the market that are not listed.
    Nick this is a good idea but i don't now if by working 2x35W on 70VA transformer can haddle the load for a long time as the transformer will be in the maximum
     
    discjockeyr, Oct 22, 2008
    #9
  10. discjockeyr

    ______.

    Joined:
    Feb 4, 2008
    Messages:
    91
    Likes Received:
    0
    Location:
    UK - London
    :confused: :confused: :confused: A transformer rated at 70VA can handle 70VA for it's life time. 70VA is the maxium it can run at and it's fine to do so.
     
    ______., Oct 22, 2008
    #10
  11. discjockeyr

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    The other thing to bear in mind is that if you do this, the globe can only be replaced with another 35W (or lower) rating... if some time in the future someone comes along and replaces a 35W with a 50W then they may have problems.

    This is probably fine if it's your own house, but maybe not if it's an installation you're handing over to someone else.

    Nick
     
    NickD, Oct 23, 2008
    #11
  12. discjockeyr

    discjockeyr

    Joined:
    Jan 9, 2007
    Messages:
    59
    Likes Received:
    0
    Yes Nick you are correct. Is better to use 105VA to be sure that will not exceed the capacity by any mistake. All depends what trannies i can find in local market.
     