Univeral 2.5AMP Dimmer

Discussion in 'C-Bus Wired Hardware' started by mann_rj, Mar 27, 2007.

  1. mann_rj

    mann_rj

    Joined:
    Mar 3, 2007
    Messages:
    11
    Likes Received:
    0
    Location:
    Melbourne
    Hi,

    Does anyone have practical experience with low voltage halogens on the relatively new L5504D2U Universal 2.5Amp per channel dimmers?

    My electrician has done 2 CBus installs and is convinced that he can only run 4 transformers from one channel.

    I would have thought that 240V x 2.5A = 600W, therefore you could run 6 x 50W halogens quite comfortably.

    If I can run 6 lights, then I save on extra equipment, so I need to understand if he is right or wrong?

    He also seems to think that those dimmers require something more than just a 10A supply to run the channels. Is he right? My reading is that the system requires 1 x 10A circuit to power 4 x 2.5A channels.

    Thanks.
    Richard
     
    mann_rj, Mar 27, 2007
    #1
  2. mann_rj

    filpee

    Joined:
    May 31, 2006
    Messages:
    204
    Likes Received:
    0
    Location:
    Western Australia
    I have used these dimmers before to fix some issues with large load and excessive transformers. From memory the largest circuit connected was..

    8x60VA Atco Possum transformers. Each transformer was connected to 2x20W Halogen lamps. Should be a theoretical 2.3A.

    I think we also installed an inductor filter module.

    These dimmers work different to the older ones. Each circuit has its own feed so you can supply individual 10A circuits to each load if you really wish.
    Also the outputs work in 2 pairs at 5 amps each. For example...

    These configs are valid
    Ch 1 = 3A, Ch 2 = max 2A, Ch 3 = 2.5A, Ch 4 = max 2.5A
    Ch 1 = 1A, Ch 2 = max 3A, Ch 3 = 2A, Ch 4 = max 3A

    This config isnt
    Ch 1 = 3A, Ch 2 = 3A, Ch 3 = 2A, Ch 4 = 2A

    Or so I have been lead to belive.

    Regards
    Phil
     
    filpee, Mar 27, 2007
    #2
  3. mann_rj

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,431
    Likes Received:
    64
    Location:
    Adelaide
    It's actually slightly better than that... if you look at the installation instructions, you'll see that you can put 600W of *lamps* on each channel (assuming incandescent or low voltage electronic transformer load types):

    L5504D2U Installation Instructions.

    I suspect your electrician is used to the older L5505D2A DIN dimmers where the limit *is* 2A per channel.

    Nick
     
    Last edited by a moderator: Mar 27, 2007
    NickD, Mar 27, 2007
    #3
  4. mann_rj

    mann_rj

    Joined:
    Mar 3, 2007
    Messages:
    11
    Likes Received:
    0
    Location:
    Melbourne
    Thanks Nick and Phil.

    Maybe he is basing it on the 1A Dimmer channels? That would only allow 4 transformers with 50W halogens.
     
    mann_rj, Mar 27, 2007
    #4
  5. mann_rj

    JohnC

    Joined:
    Apr 6, 2005
    Messages:
    554
    Likes Received:
    1
    Location:
    Sydney
    I have recently done some proper power measurements on transformers

    It's probably the VA (which includes Power Factor) that matters... so :

    Osram "Mouse" HTM70
    1 x 50W lamp : 53W 0.995PF 56.15VA
    1 x 35W lamp : 39W 0.993PF 39.28VA
    2 x 35W lamp : 75W 0.996PF 75.65VA

    Atco TM50A-2 (black wirewound)
    1 x 50W lamp : 60W 0.940PF 63.38VA
    1 x 35W lamp : 48W 0.902PF 53.26VA

    Let's allow 60VA for a 1 x 50W lamp (to be safe)... Thus at 240V :

    2.5A = 600VA - And that means that you can connect 10 per channel

    3.0A = 720VA - which means you could connect 12 to TWO of the "opposing" channels (as per filpee's post)

    The electrician is becoming confused because of the CAPACITANCE limits on the older Leading Edge Dimmers.
     
    JohnC, Mar 27, 2007
    #5
  6. mann_rj

    mann_rj

    Joined:
    Mar 3, 2007
    Messages:
    11
    Likes Received:
    0
    Location:
    Melbourne
    That is very clear and certainly explains why I have been concerned.

    Thanks for everyone's help.

    Richard
     
    mann_rj, Mar 27, 2007
    #6
  7. mann_rj

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    Interesting as I cant find anything like that int he instructions.

    So what you are saying that as long as you don't exceed 5A on the two adjacent channels you will be fine. - does that include
    Ch 1 = 1A, Ch 2 = max 4A, Ch 3 = 2A, Ch 4 = max 3A

    You can see that Ch 2 has exceeded the 2.5A by quite a way, but the total of Ch1 and Ch 2 is still only 5A.

    Just to re-iterate, capacitance of the electronic transformers is now not an issue with this dimmer?

    Mick
     
    znelbok, Mar 27, 2007
    #7
  8. mann_rj

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,431
    Likes Received:
    64
    Location:
    Adelaide
    No... you can't do this. If my memory serves me correctly the installation instructions *used* to say that you could load a channel up to 3A if you de-rated both adjacent channels to 2A. I suspect we may have updated them to remove confusion such as above.

    It comes down to the fact that the limit is the thermal capability of the heatsink, but 4A on a channel is getting into the territory where the cold start will start to trip the short circuit protection of the channel.

    That's correct. The Universal DIN dimmer operates in trailing edge mode for electronic transformer loads, so capacitance isn't an issue. It actually always starts in trailing edge mode, and automatically switches over to leading edge mode if the load type detected warrants it. You can tell which mode each channel is operating in from the indicator colour on the unit.

    Nick
     
    NickD, Mar 28, 2007
    #8
  9. mann_rj

    filpee

    Joined:
    May 31, 2006
    Messages:
    204
    Likes Received:
    0
    Location:
    Western Australia
    Yeah.. what NickD says. I forgot to mention in my post that 3 Amps was the max. Sorry about that.
     
    filpee, Mar 28, 2007
    #9
  10. mann_rj

    JohnC

    Joined:
    Apr 6, 2005
    Messages:
    554
    Likes Received:
    1
    Location:
    Sydney
    I found the document that talks about 3A... it was an "internal" information sheet thingy ( note the spelling :rolleyes: ) - dated 10/8/06 with the title :

    n e w p r o d u c t f e a t u r e s a n d b e n i f i t s

    Four independent dimmer channels, with each channel
    capable of controlling up to 2.5A of load (i.e., 10A
    maximum load per dimmer unit).
    (Note: Up to 3A may be connected to a channel, as long
    as any adjacent channels are not loaded to more than
    2A).


    I can't see any subsequent info that makes mention of this 3A, so I am thinking that perhaps CIS decided not to make a point of it (due to confusion by installers), or have re-evaluated the maximum ratings and have left it at 4x2.5A for reliability's sake.
     
    JohnC, Mar 28, 2007
    #10