Unusual dimmer behaviour

Discussion in 'C-Bus Wired Hardware' started by Deano, Jun 25, 2013.

  1. Deano

    Deano

    Joined:
    Sep 8, 2008
    Messages:
    9
    Likes Received:
    0
    Hey everyone.

    Having some issues with a new C-Bus install at the moment whereby dimmed circuits that are ON will turn OFF for a couple of secs and then ON again upon the client pushing a C-Bus switch or if detected by a motion sensor in the pantry. It's definitely not a programming issue as the fault is intermittant and can't be replicated. It doesn't appear to be affecting relay switched circuits.

    I have been suspecting a possible mains supply issue? Overvoltage maybe? When the intermittant fault occurs all CBUS units appear ok, no flashing of lights on switches or output hardware occur. The house then returns to normal operation. This one has me beat.

    Have used the Universal Dimmers on other installs and never seen an install with this problem before. Any ideas.

    Thanks,
    Deano
     
    Deano, Jun 25, 2013
    #1
  2. Deano

    7iron

    Joined:
    Dec 18, 2008
    Messages:
    59
    Likes Received:
    0
    Location:
    Melbourne
    Hi

    I've had a problem like this which was low mains voltage on one phase impacting the one relay unit on that phase.

    in my case the C-bus status lights on the relay went off i.e all LEDs on the C-bus relay go off including the C-bus network LEDS. The phase was dropping to 190v

    Cheers
    Michael
     
    7iron, Jun 25, 2013
    #2
  3. Deano

    MarkWES

    Joined:
    Jan 28, 2013
    Messages:
    3
    Likes Received:
    0
    Location:
    Perth
    I'm having exactly the same issue with 2 channels on a universal dimmer. Each channel has only 5x 50w halogen globes using clipsal hunter electronic transformers???
     
    MarkWES, Jun 25, 2013
    #3
  4. Deano

    jboer

    Joined:
    Apr 27, 2012
    Messages:
    458
    Likes Received:
    35
    Location:
    Sydney
    Hey,

    I have seen this on one job. It was due to electronic transformers and the induction of the in rush into other cables I believe. The Universal dimmer then gets confused about what load is on it and turns off, or something like that. I am sure one of the experts might be able to help with a more technical explanation.

    Anyway we were put on to the Inductor Filter Modules and it appears to have worked a treat. Clipsal Product Link Might be worth a try?
     
    Last edited by a moderator: Jun 27, 2013
    jboer, Jun 25, 2013
    #4
  5. Deano

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    The high inrush current present with some electronic loads (and cheap LED lamps are the worst) causes such a large current spike that it can cause the short-circuit protection in the dimmer to activate. The dimmer needs to shut the channel down at some point to protect itself and it seems that some of these cheap lamps can have inrush currents large enough to trip the protection circuitry. The dimmer channel re-starts itself after a second or two. After a couple of tries it gives up, requiring you to turn the channel off and then on again.

    If the magnitude of the current spike isn't too large then you can usually knock it down a fair bit by using a 32EIND. It's definitely worth a shot.
     
    Newman, Jul 8, 2013