    I need to add a new relay which will be located approx 70m from the main coms room in the house, which houses most of the C-Bus relays etc. The network this new relay will be on currently consumes 1652ma and has 1800ma of supply.

    Given the distance my preference is to install a powered relay to avoid possible voltage drops. This will put me at the 2A limit. Is there any downside to running the full 2A when only drawing 1652ma from the system.

    Thanks

    Andrew
     
    abg, Nov 16, 2009
    #1
  2. abg

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    That should be fine. The units will only draw the current they need, so adding extra power supply will not increase the current draw.

    The 2A limit is mainly there in case of short-circuits in the wiring.
     
    Darren, Nov 16, 2009
    #2
  3. abg

    Don

    Joined:
    Aug 4, 2004
    Messages:
    429
    Likes Received:
    0
    Location:
    Townsville, Australia
    No.

    The 2A limit is imposed because of the rating of the C-Bus cable. Over this, and there is a risk of cable damage due to excessive temperatures. This may be a concern depending on where your cabling runs relative to sources of heat (note that sources of heat include other cables carrying current) and proximity to thermal insulation. It's a difficult problem to define precisely in each installation, hence the cable has been given a rating of 2A which can be used as a guideline.

    Running a C-Bus network at the 2A limit will not stress any other component of the system.
     
    Don, Nov 16, 2009
    #3
  4. abg

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    If that relay is the only thing at the end of the 70m cable run, then the voltage drop will be tiny - the relay probably only draws <22mA, which, if you're using 2 pairs, at ~90ohms/km, is only a drop of about 0.14V over 70m.

    Nick
     
    NickD, Nov 16, 2009
    #4
  5. abg

    abg

    Joined:
    Dec 25, 2007
    Messages:
    208
    Likes Received:
    2
    Location:
    Sydney
    The C-Bus cable is in an underground conduit with a couple of Cat 6 cables and shielded security cables so is well isolated. Will go with the L5508RVF for this one. Many thanks for the quick response.
     
    abg, Nov 16, 2009