Wiring instructions for shutter relays

Discussion in 'C-Bus Wired Hardware' started by 2SC, Jan 28, 2010.

  1. 2SC

    2SC

    Joined:
    Oct 10, 2006
    Messages:
    345
    Likes Received:
    0
    Location:
    Athens, Greece
    Checking the installation instructions of the L5501RBCP, I saw in Figure 1 that the shutter relay distributes neutral on the shutter motor.

    I was wondering if this is important for the correct function of the shutter relay. I mean if I wire neutral from the same neutral bar to both shutter relay and shutter motor isn't it the same?
     
    2SC, Jan 28, 2010
    #1
  2. 2SC

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    The shutter relay unit breaks both the active and the neutral connection to the motor when the motor is stopped. This is a requirement in some markets where C-Bus products are sold. It also makes it fairly easy to wire the motor up, as you just run a single feed all the way back to the Shutter Relay unit, although this is a fairly minor point.

    The neutral connections can be left un-connected as it is not a required connection for correct operation, provided you are meeting the wiring regulations in your country.
     
    Newman, Jan 28, 2010
    #2
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.